I woke up this morning to a text from my ISP, “There is an outage in your area, we are working to resolve the issue”

I laugh, this is what I live for! Almost all of my services are self hosted, I’m barely going to notice the difference!

Wrong.

When the internet went out, the power also went out for a few seconds. Four small computers host all of my services. Of those, one shutdown, and three rebooted. Of the three that ugly rebooted some services came back online, some didn’t.

30 minutes later, ISP sends out the text that service is back online.

2 hours later I’m still finding down services on my network.

Moral of the story: A UPS has moved to the top of the shopping list! Any suggestions??

  • @[email protected]
    link
    fedilink
    English
    113
    edit-2
    10 months ago

    When you are bored, backup a VM then hard kill it and see if it manage to restart properly.
    Software should be able to recover from that.
    If it doesn’t, troubleshoot.

    • Deebster
      link
      fedilink
      English
      1610 months ago

      That reminds me of Netflix’s Chaos Monkey (basically in office hours this tool will randomly kill stuff).

    • @[email protected]
      link
      fedilink
      English
      1110 months ago

      When I built my home server this is what I did with all VMs. Learned how to change the start up delay time in esxi and ensured everything came back online with no issues from a cold built.

      Rip VMware.

    • @[email protected]
      link
      fedilink
      English
      410 months ago

      While I appreciate the sentiment, most traditional VMs do not like to have their power killed (especially non-journaling file systems).

      Even crash consistent applications can be impacted if the underlying host fs is affected by power loss.

      I do think that backup are a valid suggestion here, provided that the backup is an interrupted by a power surge or loss.

      • @[email protected]
        link
        fedilink
        English
        4310 months ago

        most traditional VMs do not like to have their power killed (especially non-journaling file systems).

        Why are you using a non-journaling file system in 2024 when those were common 10+ years ago?

          • @[email protected]
            link
            fedilink
            English
            210 months ago

            I would still consider that generation of filesystem to be effort to use while regular journaling filesystems have been so ubiquitous that you need to invest effort to avoid using one.

              • @[email protected]
                link
                fedilink
                English
                110 months ago

                Maybe on some distros that is the case if you install a recent version but to get a non-journaling filesystem you literally have to partition manually to avoid using one on any distro that is still supported today and meant for full sized PCs (as opposed to embedded devices).

        • lazynooblet
          link
          fedilink
          English
          410 months ago

          It’s been a while since a power cut affected my services, is this why?

          I remember having to troubleshoot mysql corruption following abrupt power loss, is this no longer a thing?

          • @[email protected]
            link
            fedilink
            English
            810 months ago

            Databases shouldn’t even need a journaling filesystem, they usually pay attention to when to use fsync and fdatasync.

            In fact journaling filesystems basically use the same mechanisms as databases only for filesystem metadata.

      • Possibly linux
        link
        fedilink
        English
        1310 months ago

        Your system should be fine after a hard kill. If its not stop using it as that’s going to be a problem down the road.

  • lemmyvore
    link
    fedilink
    English
    4010 months ago

    IMHO you’re optimizing for the wrong thing. 100% availability is not something that’s attainable for a self-hoster without driving yourself crazy.

    Like the other comment suggested, I’d rather invest time into having machines and services come back up smoothly after reboots.

    That being said, an UPS may be relevant to your setup in other ways. For example it can allow a parity RAID array to shut down cleanly and reduce the risk of write holes. But that’s just one example, and an UPS is just one solution for that (others being ZFS, or non-parity RAID, or SAS/SATA controller cards with built-in battery and/or hardware RAID support etc.)

    • @[email protected]
      link
      fedilink
      English
      1910 months ago

      I agree that 99.999% uptime is a pipedream for most home labs, but I personally think a UPS is worth it, if only to give yourself the option to gracefully shut down systems in the event of a power outage.

      Eventually, I’ll get a working script that checks the battery backup for mains power loss and handle the graceful shutdown for me, but right now that extra 10-15 minutes of battery backup is enough for a manual effort.

      • shnizmuffin
        link
        fedilink
        English
        910 months ago

        Some of the nicer models of UPS have little servers built in for remote management, and also communicate to their tenants via USB or Serial or Emergency Power Off (EPO) Port.

        You shouldn’t have to write a script that polls battery status, the UPS should tell you. Be told, don’t ask.

      • JustEnoughDucks
        link
        fedilink
        English
        210 months ago

        The problem is that for most self-hosters, they would be working and unavailable to do a graceful shutdown in any case even if they had a UPS unless they work fully from home with 0 meetings. If they are sleeping or at work, (>70% of the day for many or most) then it is useless without graceful shutdown scripts.

        I just don’t worry about it and go through the 10 minute startup and verification process if anything happens. Easier to use an uptime monitor like uptimekuma and log checker like dozzle for all of your services available locally and remotely and see if anything failed to come back up.

  • @[email protected]
    link
    fedilink
    English
    3610 months ago

    Did the services fail to come back due to the bad reboot, or would they have failed to come back on a clean reboot? I ugly reboot my stuff all the time, and unless the hardware fails, i can be pretty sure its all going to come back. Getting your stuff to survive reboot is probably a better spend of effort.

    • PadookOP
      link
      fedilink
      English
      1610 months ago

      I didn’t mean to imply that Services actually broke. Only that they didn’t come back after a reboot. A clean reboot may have caused some of the same issues because, I’m learning as I go. Some services are restarted by systemctl, some by cron, some…manual. This is certainly a wake up call that I need standardize and simplify the way the services are started.

      • @[email protected]
        link
        fedilink
        English
        1710 months ago

        We’ve all.committed that sin before. Its better to rely on it surviving the reboot than to try prevent the reboot.

        Also worth looking into some form of uptime monitoring software. When something goes down, you want to know about it asap.

        And documenting your setup never hurts :D

        • Nimmo
          link
          fedilink
          English
          510 months ago

          On the uptime monitoring I’ve been quite happy with uptime kuma, but… If you put it on the same host that’s down… Well, that’s not going to work :p (I nearly made that mistake)

          • @[email protected]
            link
            fedilink
            English
            310 months ago

            It’s not the most detailed thing, but I just use a free account on cron-job.org to send a head request every two minutes to a few services that are reachable from the internet (either just their homepage or some ping endpoint in the API) and then used the status page functionality to have a simple second status page on a third party server.

            You can do a bit more on their paid tier, but so far I didn’t need that.

            On the other hand, you could try if a free tier/cheap small vps on one of the many cloud providers is sufficient for an uptime Kuma installation. Just don’t use the same cloud provider as all other of your services run in.

            • Nimmo
              link
              fedilink
              English
              210 months ago

              Oh, I’m fine with my setup, I have a couple of external servers that can monitor all my web accessible stuff with kuma and then I’ve got another local one to monitor my non-web accessible stuff.

              Thanks for those tips though, definitely useful to consider other options

          • @[email protected]
            link
            fedilink
            English
            310 months ago

            Same, Uptime Kuma is fantastic. I put it on my most critical server, if Kuma is down, everything is down :D

      • @iknowitwheniseeit
        link
        English
        210 months ago

        I reboot every box monthly to flush out such issues. It’s not perfect, since it won’t catch things like circular dependencies or clusters failing to start if every member is down, but it gets lots of stuff.

    • @[email protected]
      link
      fedilink
      English
      1210 months ago

      Yeah an unclean reboot shouldn’t break anything as long as it wasn’t doing anything when it went down. I’ve never had any issues when I have to crash a computer unless it was stuck doing an update.

    • BreakDecks
      link
      fedilink
      English
      2810 months ago

      My favorite part about using an old laptop as a 24/7/365 plugged-in server is the anticipation of when the lithium battery will explode from overcharging.

      • @[email protected]
        link
        fedilink
        English
        4510 months ago

        “overcharging” doesn’t exist. There are two circuits preventing the battery from being charged beyond 100%: the usual battery controller, and normally another protection circuit in the battery cell. Sitting at 100% and being warm all the time is enough for a significant hit on the cell’s longetivity though. An easy measure that is possible on many laptops (like thinkpads) is to set a threshold where to stop charging at. Ideal for longetivity is around 60%. Also ensure good cooling.

        Sorry for being pedantic, but as an electricial engineer it annoys me that there’s more wrong information about li-po/-ion batteries, chargers and even usb wall warts and usb power delivery than there’s correct information.

        • @[email protected]
          link
          fedilink
          English
          310 months ago

          Isn’t dendrite formation and the shorts they can cause a much bigger concern when dealing with old batteries that are being charged 24/7? Asking a genuine question here, so please don’t shoot me if I’m wrong. 🙂 I’d love to hear more about the most common failure modes and causes for li-po/ion batteries.

          • @[email protected]
            link
            fedilink
            English
            6
            edit-2
            10 months ago

            Those are symptoms of sitting at that operation point permanently, and they are a of course a concern. What I’m after is that people think that energy gets put in to the battery, i.e. it gets charged, as long as a “charger” is connected to the device (hence terms like “overcharged”). But that is not true, because what is commonly referred to as “charger” is no charger. It is just a power supply and has literally zero say in if, how and when the battery gets charged. It only gets charged if the charge controller in the device decides to do that now, and if the protection circuit allows it. And that is designed to only happen if the battery is not full. When it is full, nothing more happens, no currents flow in+out of the battery anymore. There’s no damage due to being charged all the time, because no device keeps on pumping energy into the cell if it is full.

            There is however damage from sitting (!) at 100% charge with medium to high heat. That happens indipendently from a power supply being connected to the device or not. You can just as well damage your cells by charging them to 100% and storing them in a warm place while topping them of once in a while. This is why you want to have them at lower room temperature and at ~60%, no matter if a device/“charger” is connected or not.

            (Of course keeping a battery at 60% all the time defeats the purpose of the battery. So just try to keep it cool, charged to >20% and <80% most of the time, and you’re fine)

        • 486
          link
          fedilink
          2
          edit-2
          10 months ago

          For many li-ion laptop batteries, the manufacturer’s configuration of a 100 % charge is pretty much equivalent to overcharging. I’ve seen many laptops over the years with swollen batteries, almost all of them had been plugged in all the time, with the battery kept at 100 % charge.

          As an electrical engineer you should know that technically there is no 100 % charge for batteries. A battery can more or less safely be charged up to to a certain voltage. The 100 % charge point is something the manufacturer can choose (of course within limits depending on cell chemistry). A manufacturer can choose a higher cell voltage than another to gain a little more capacity, at the cost of longterm reliability. There are manufacturers that choose a cell voltage of 4250 mV and while that’s possible and works okay if charged only occasionally, if plugged in all the time, this pretty much ensures killing the batteries rather quickly. I would certainly call that overcharging.

          Since you already mentioned charging thresholds, I just want to say, anyone considering using a laptop as a server should absolutely make use of this feature and limit the maximum charge.

      • λλλ
        link
        fedilink
        English
        210 months ago

        Amen. I appreciate my UPS for sure!

  • Deebster
    link
    fedilink
    English
    1810 months ago

    A general tip on buying UPSes: look for second hand ones - people often don’t realise you can just replace the battery in them (or can’t be bothered) so you can get fancier/larger ones very cheap.

    • @[email protected]
      link
      fedilink
      English
      1010 months ago

      Also, a larger capacity one is better, and it’s likely you’ll find a secondhand one with more capacity/features for a similar price.

      • @[email protected]
        link
        fedilink
        English
        2
        edit-2
        10 months ago

        Why? If the power has gone out there are very few situations (I can’t actually think of any except brownouts or other transient power loss) where it would be useful to power my server for much longer than it takes to shut down safely.

        • Deebster
          link
          fedilink
          English
          310 months ago

          Longer means you’re more likely to be able to ride out a power cut, and gives you more options if you want/need to complete something more involved than saving and shutting down.

  • @[email protected]
    link
    fedilink
    English
    1710 months ago

    Though I wonder if even besides adding an uninterruptible power supply (UPS) (writing acronym out for anyone else who would’ve had to Google it), this might be a useful exercise recovering from outages in general. This is coming from someone who hasn’t actually done any self hosting of my own, but you saying you’re still finding down services reminds me of when I learned the benefit of testing system backups as part of making them.

    I was lucky in that I didn’t have any data loss, but restoring from my backup took a lot more manual work than I’d anticipated, and it came at an awkward time. Since then, my restoring from backup process is way more streamlined.

  • @[email protected]
    link
    fedilink
    English
    1510 months ago

    This is why I gave up self hosting. It’s great when it works but it just becomes an expensive second job. I still have Plex/Jellyfin etc but for emails and password vaults I just pay for external services.

      • PadookOP
        link
        fedilink
        English
        1210 months ago

        I could have the best self hosted setup… living in a van, down by the river!

    • @[email protected]
      link
      fedilink
      English
      610 months ago

      I like to host as many services as possible and I’m fine with it being a second job at times since this is my main hobby, but I actually agree with you on your examples. The three things I won’t self-host are:

      1. Emails - I am not willing to put in the effort on this. Plus, my ISP blocks those ports so I’d already be into using a VPS even if I wanted to host this. I’d rather just pay someone else, like Proton.

      2. Password manager - I actually did self-host Bitwarden for a long time, but after thinking about it for a while, I decided to take the pay someone else approach here too. I’m pretty sure I’m doing everything correctly, but I’m not a security expert. I’d rather be 100% sure my passwords are in safe hands rather than be 95% sure that I’m doing everything right on this one.

      3. Lemmy - I’ve heard about (luckily never seen) CSAM attacks on Lemmy/Kbin and will not risk that kind of content being downloaded because I’m federated with an instance dealing with those attacks. I’m happy to throw a couple bucks at lemmy.world’s Patreon and let them handle that.

    • jelloeater - Ops Mgr
      link
      fedilink
      English
      310 months ago

      I self host stuff that I feel the need to. But TBH, you don’t really need to self host much, outside of media collections. PhotoPrism and JellyFin are about the only two I need, aside from a PiHole. Most folks would be fine with a beefy NAS.

  • Jo Miran
    link
    fedilink
    English
    1310 months ago

    A UPS should always be your first or second purchase if only for power conditioning and brown-out protection.

    • @[email protected]
      link
      fedilink
      English
      210 months ago

      They will do power conditioning? My modem is such a sensitive baby I cannot plug anything else in next to it or it starts dropping packets. Would a UPS help with that? Unfortunately I cannot replace the modem, that’s the only one the ISP will give me.

        • @[email protected]
          link
          fedilink
          English
          2
          edit-2
          10 months ago

          FYI Few downside of an online/double conversion UPS will use extra power if that is something your trying to avoid.

          Also some of them will have a 24/7 fan so there will be extra noise.

  • @[email protected]
    link
    fedilink
    English
    1210 months ago

    I’m a big fan of running home stuff on old laptops for this reason. Most UPSs give you a few minutes to shut down, laptops (depending on what you run) could give you plenty of extra run time and plenty of margin for a shutdown contingency.

    • @Drewelite
      link
      English
      910 months ago

      Small, good value, quiet, power efficient, built in battery backup and server terminal. Laptops are dope for home labs!

  • @[email protected]
    link
    fedilink
    English
    1010 months ago

    This is why I have about five of these bad boys: CyberPower CP1500PFCLCD.

    One is in my utility room for my cable modem and our chest freezer, three back up my homelab and wifi AP, and one is for my office.

    They’ve been bulletproof through storms, and when we’ve lost power, but not Internet I can’t keep on working.

    The big thing to look for is number of battery+surge outlets vs just surge outlets. Typically they top out at 1500VA - the more overhead for what you’re powering, the longer you can go without mains power.

    A screen/display is helpful for at-a-glance information like expected runtime, current output, etc.

    • @[email protected]
      link
      fedilink
      English
      410 months ago

      Never heard of someone using a UPS on a Fridge/Freezer. Does it make a difference? Seems like the UPS would just died after 10-20 minutes and not really make much difference to your freezer.

      • @[email protected]
        link
        fedilink
        English
        310 months ago

        I didn’t intend to use it on the chest freezer - it was mostly for the modem, but since I had spare battery capacity and outlets I thought what the heck.

        The power load is practically nothing until it cycles, and even then it’s fairly efficient - my current runtime is estimated to be about 18 hours, more than enough to come up with an alternative if we lose power in a storm.

  • ChojinDSL
    link
    fedilink
    English
    910 months ago

    UPS with usb allows you to configure a script to properly shutdown your server when a power outage happens and the UPS battery is about to run out.